(A) Given: Power $P = 800 \; kW = 8 \times 10^5 \; W$,Voltage at town $V_1 = 40,000 \; V$,Distance $d = 15 \; km$,Resistance per unit length $r = 0.5 \; \Omega/km$.
Total resistance $R = (15 + 15) \times 0.5 = 15 \; \Omega$.
Current in the line $I = P / V_1 = (800 \times 10^3) / 40,000 = 20 \; A$.
$(a)$ Line power loss $P_{loss} = I^2 R = (20)^2 \times 15 = 400 \times 15 = 6,000 \; W = 6 \; kW$.
$(b)$ Total power supplied by the plant $P_{total} = P + P_{loss} = 800 \; kW + 6 \; kW = 806 \; kW$.
$(c)$ Voltage drop in the line $V_{drop} = I \times R = 20 \times 15 = 300 \; V$. Voltage at the output of the step-up transformer $V_{out} = V_1 + V_{drop} = 40,000 + 300 = 40,300 \; V$. Since the plant generates at $440 \; V$,the step-up transformer is $440 \; V - 40,300 \; V$.
High-voltage transmission is preferred because power loss $P_{loss} = I^2 R = (P/V)^2 R$ is inversely proportional to the square of the transmission voltage $V^2$. Increasing $V$ significantly reduces $I^2 R$ losses.